PARIXO GATE · ME Open the app

GATE 2018 ME Set 2 · Question 53

2 marksNumerical answerThermodynamicsRefrigeration Cycles (VCRS and Bell-Coleman)

A standard vapor compression refrigeration cycle operating with a condensing temperature of and an evaporating temperature of develops of cooling. The - diagram shows the enthalpies at various states. If the isentropic efficiency of the compressor is , the magnitude of compressor power (in kW) is ________ (correct to two decimal places).

Figure 1 for GATE 2018 ME Set 2 question 53

GATE 2018 · Mechanical Engineering · Set 2 · IIT Guwahati · printed as Q.43 in the ME section

Answer
9.5 to 10.5

From the official answer key published by IIT Guwahati.

Worked solution

From the given - diagram:

  • Saturated vapor enthalpy at compressor inlet:
  • Isentropic compressor discharge enthalpy:
  • Saturated liquid enthalpy at condenser exit:
  • Enthalpy after throttling:

The refrigerating effect per unit mass is:

Given the cooling capacity , the mass flow rate of refrigerant is:

The isentropic work of compression per unit mass is:

Given the isentropic efficiency , the actual work of compression is:

The actual compressor power is:

Answer: 10 (or 10.00)

Practise Refrigeration Cycles (VCRS and Bell-Coleman)

12 GATE questions from this chapter, in short untimed sets, with the formula sheet beside them. Free.

More from Refrigeration Cycles (VCRS and Bell-Coleman)

Question from the official GATE 2018 ME paper (Set 2), IIT Guwahati. Solutions by PARIXO AI. All 65 questions of this paper.