An air-conditioning system provides a continuous flow of air to a room using an intake duct and an exit duct, as shown in the figure. To maintain the quality of the indoor air, the intake duct supplies a mixture of fresh air with a cold air stream. The two streams are mixed in an insulated mixing chamber located upstream of the intake duct. Cold air enters the mixing chamber at , with a volume flow rate of during steady state operation. Fresh air enters the mixing chamber at and . The mass flow rate of the fresh air is times of the cold air stream. Air leaves the room through the exit duct at .

Assuming the air behaves as an ideal gas with and , the rate of heat gain by the air from the room is ________ *(round off to two decimal places)*.

Figure 1 for GATE 2021 ME Set 1 question 59

GATE 2021 · Mechanical Engineering · Set 1 · IIT Bombay · printed as Q.49 in the ME section

Answer
4.9 to 5.1

From the official answer key published by IIT Bombay.

Worked solution

For the cold air stream, treating air as an ideal gas:

The mass flow rate of the fresh air is , giving a total mass flow rate:

An energy balance on the insulated mixing chamber yields the mixture temperature :

The rate of heat gain by the air from the room as it exits at is:

Answer: 4.96