GATE 2015 ME Set 2 · Question 52
A balanced counterflow heat exchanger has a surface area of and overall heat transfer coefficient of . Air () entering at and is to be preheated by the air leaving the system at and . The outlet temperature (in K) of the preheated air is
- A
290
- B
300
- C
320
- D
350
GATE 2015 · Mechanical Engineering · Set 2 · IIT Kanpur
Answer
From the official answer key published by IIT Kanpur.
Worked solution
For a counterflow heat exchanger, the heat capacity rates of both cold and hot streams are:
Since , this is a balanced heat exchanger with capacity ratio .
The number of transfer units () is:
For a counterflow heat exchanger with , the effectiveness is:
The effectiveness is also defined as the ratio of actual to maximum possible heat transfer:
Given and :
Answer: (A) 290
Practise Heat Exchangers: LMTD & Effectiveness-NTU Methods
19 GATE questions from this chapter, in short untimed sets, with the formula sheet beside them. Free.
More from Heat Exchangers: LMTD & Effectiveness-NTU Methods
- GATE 2015 ME Set 3 · Q22Saturated vapor is condensed to saturated liquid in a condenser. The heat capacity ratio is Cr = C C . The…
- GATE 2014 ME Set 2 · Q26In a heat exchanger, it is observed that Δ T1 = Δ T2, where Δ T1 is the temperature difference between the…
- GATE 2014 ME Set 2 · Q58In a concentric counter flow heat exchanger, water flows through the inner tube at 25°C and leaves at 42°C.…
- GATE 2014 ME Set 3 · Q58A double-pipe counter-flow heat exchanger transfers heat between two water streams. Tube side water at 19…
- GATE 2012 ME · Q41Water (Cp = 4.18 kJ/kg.K) at 80°C enters a counterflow heat exchanger with a mass flow rate of 0.5 kg/s. Air…
- GATE 2026 ME · Q55Convective heat transfer coefficients for Fluid 1 and Fluid 2 in a heat exchanger, as shown in the figure…
Question from the official GATE 2015 ME paper (Set 2), IIT Kanpur. Solutions by PARIXO AI. All 65 questions of this paper.