GATE 2021 ME Set 2 · Question 54

2 marksNumerical answerHeat TransferHeat Exchangers: LMTD & Effectiveness-NTU Methods

A shell and tube heat exchanger is used as a steam condenser. Coolant water enters the tube at at a rate of . The overall heat transfer coefficient is , and total heat transfer area is . Steam condenses at a saturation temperature of . Assume that the specific heat of coolant water is . The temperature of the coolant water coming out of the condenser is \_\_\_\_\_\_\_ *(round off to the nearest integer)*.

GATE 2021 · Mechanical Engineering · Set 2 · IIT Bombay · printed as Q.44 in the ME section

Answer
337 to 341

From the official answer key published by IIT Bombay.

Worked solution

For a steam condenser undergoing phase change at saturation temperature, the capacity ratio , as .

The heat capacity rate of the coolant water is:

The number of transfer units (NTU) is:

For a condenser (), the effectiveness is given by:

The effectiveness is also defined as:

Substituting the given values:


Answer: 339

Practise Heat Exchangers: LMTD & Effectiveness-NTU Methods

19 GATE questions from this chapter, in short untimed sets, with the formula sheet beside them. Free.

More from Heat Exchangers: LMTD & Effectiveness-NTU Methods

Question from the official GATE 2021 ME paper (Set 2), IIT Bombay. Solutions by PARIXO AI. All 65 questions of this paper.