GATE 2022 ME Set 2 · Question 64
Saturated vapor at condenses to saturated liquid at the rate of on the shell side of a heat exchanger (enthalpy of condensation ). A fluid with enters at on the tube side. If the effectiveness of the heat exchanger is , then the mass flow rate of the fluid in the tube side is ________ *(in integer)*.
GATE 2022 · Mechanical Engineering · Set 2 · IIT Kharagpur
Answer
From the official answer key published by IIT Kharagpur.
Worked solution
For a condenser, the phase-changing fluid has an infinite heat capacity rate (), so the minimum heat capacity rate is that of the cold fluid:
The total heat transfer rate is the heat released by the condensing steam:
The effectiveness of a heat exchanger with is defined as:
The heat absorbed by the tube-side fluid is:
Answer: 1000
Practise Heat Exchangers: LMTD & Effectiveness-NTU Methods
19 GATE questions from this chapter, in short untimed sets, with the formula sheet beside them. Free.
More from Heat Exchangers: LMTD & Effectiveness-NTU Methods
- GATE 2021 ME Set 2 · Q54A shell and tube heat exchanger is used as a steam condenser. Coolant water enters the tube at 300 K at a…
- GATE 2020 ME Set 1 · Q35In a concentric tube counter-flow heat exchanger, hot oil enters at 102°C and leaves at 65°C. Cold water…
- GATE 2019 ME Set 2 · Q56Hot and cold fluids enter a parallel flow double tube heat exchanger at 100 °C and 15 °C, respectively. The…
- GATE 2018 ME Set 2 · Q64Steam in the condenser of a thermal power plant is to be condensed at a temperature of 30°C with cooling…
- GATE 2017 ME Set 1 · Q10Saturated steam at 100°C condenses on the outside of a tube. Cold fluid enters the tube at 20 °C and exits…
- GATE 2017 ME Set 2 · Q46In a counter-flow heat exchanger, water is heated at the rate of 1.5 kg/s from 40 °C to 80 °C by an oil…
Question from the official GATE 2022 ME paper (Set 2), IIT Kharagpur. Solutions by PARIXO AI. All 65 questions of this paper.